mains again

Discussion in 'Hi-Fi and General Audio' started by penance, Jul 14, 2003.

  1. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    well the system is running in, but it seems tempermental, sometimes open and sometimes muddled
    so i rekon its time to take the mains serious:eek:

    Im going to stick in a dedicated spur and im thinking of useing the following

    2 * MK unswitched metal clad double sockets with surface patress
    1 gang distribution box
    16mm2 tails
    2 core 2.5mm2 SWA
    6mm2 earth cable

    plan -
    from existing box use tails into new box
    connect SWA armour and 6mm2 earth to earth at disty box
    run SWA up outside of house into upstairs listening room
    into first socket but only useing the seperate earth and insulating the SWA armour so as it is used purely as an RFI screen on the cable

    so thats the basic idea, what do you think?
     
    penance, Jul 14, 2003
    #1
  2. penance

    wadia-miester Mighty Rearranger

    Joined:
    Jun 19, 2003
    Messages:
    6,026
    Likes Received:
    0
    Location:
    Beyond the 4th Dimension
    I think you have done this before :)
     
    wadia-miester, Jul 14, 2003
    #2
  3. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    LoL
    nope
    jut an ex sparky, but with no knowledge of hifi specific cableing

    sounds like a plan then?
     
    penance, Jul 14, 2003
    #3
  4. penance

    wadia-miester Mighty Rearranger

    Joined:
    Jun 19, 2003
    Messages:
    6,026
    Likes Received:
    0
    Location:
    Beyond the 4th Dimension
    Should surfice, what switchbox and MCB's are u going to use?, I would personaly use different wire (because I'm that way inclined and I did get some rather good trick cyro'd stuff at a nice price), maybe the hospital grade 60 amp stuff?, I know your not going to use 60 amps, but you may be surprised at the difference I think The mad hippy is more the man to ask here, but judging by you list a fair start, and not much dosh involved too. WM
     
    wadia-miester, Jul 14, 2003
    #4
  5. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    i may go up to 4mm2, depends on price
    idealy i would like to use Mineral Insulated, but cant justify the cost at the mo (cuz i want some guys trichord aswell;) ), but it would give copper shield :)

    unsure on disty unit, but ill see if i can get a metal clad 1 gang for not to much, probably MK mcb, but may try good old re-wirable fuse to start

    so whats the good price on the cyro stuff hmmm?:D
     
    penance, Jul 14, 2003
    #5
  6. penance

    wadia-miester Mighty Rearranger

    Joined:
    Jun 19, 2003
    Messages:
    6,026
    Likes Received:
    0
    Location:
    Beyond the 4th Dimension
    A little bit more than the trichord :)
     
    wadia-miester, Jul 14, 2003
    #6
  7. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    hmm
    bet you aint got 30M of the stuff;)

    Just looked, and i think 4mm2 is within budget:)

    im after any advice on it that will help improve without costing the same as the amp i want:cool:
     
    penance, Jul 14, 2003
    #7
  8. penance

    bottleneck talks a load of rubbish

    Joined:
    Jun 19, 2003
    Messages:
    6,766
    Likes Received:
    1
    Location:
    bucks
    Hi Penance,

    You might want to call Russ Andrews, he publishes a little leaflet on the topic. I remember that amongst the tweaks mentioned were using an earth spike buried in the garden....

    I cant remember 1/2 of it, and as a sparky it would probably make a lot more sense to you anyway than I!

    NB
    You could have a nice little earner doing this for your audiophile mates... £50 cash plus petrol?!?!? heehheee

    chris
     
    bottleneck, Jul 14, 2003
    #8
  9. penance

    GrahamN

    Joined:
    Jun 20, 2003
    Messages:
    572
    Likes Received:
    0
    Location:
    Suwway
    A little bird tells me that the hot tip in DIY circles is that annealing does a similar job to cryo treating. As this is probably a far more widespread technique, maybe wire of that nature would be easier (and cheaper) to source - although maybe it doesn't work to the kind of gauge you need.

    Shouldn't this thread really be in the DIY forum?
     
    GrahamN, Jul 14, 2003
    #9
  10. penance

    themadhippy seen it done it smokin it

    Joined:
    Jun 19, 2003
    Messages:
    1,118
    Likes Received:
    1
    Location:
    by the cross
    penance how are you going to tap into the mains? a henley block is the easiest,saves messing around in the consumner unit,just make sure the new tails are the same size as the old tails,also why the extra earth condutor?why not 3 core swa? makes thing easier/cheaper
     
    themadhippy, Jul 14, 2003
    #10
  11. penance

    HenryT

    Joined:
    Jun 19, 2003
    Messages:
    1,288
    Likes Received:
    0
    Location:
    Devon, UK
    Depends if you're planning on carrying out the work yourself, I guess. I know I wouldn't, seeing as I'm not a qualified sparky! :)

    Very interesting thread anyway. Sort of stole my thunder with this one, as I've been muling over the plans for a dedicated mains set-up for a while now. Probably won't do anything about it this year, at present just thinking about it all and sorting out what materials to use. Don't mind throwing a bit of cash it.

    I've got tons of questions myself, especially on what sort of wiring to use to the plugs/socket connections.

    SWA cable is no doubt the cheapest form of shielded wiring. A right royal pain to work with I'd imagine, but then that's what you pay a sparky for I suppose if you haven't got the practical capability or inclinnation to DIY.

    WM's cryo stuff looks interesting for the in wall wiring. I was also thinking about this stuff (which is at least BS approved apparently):

    http://www.britishaudio.co.uk/loradflt.htm

    and these distribution boards (namely the 6 way jobby for my proposed system):

    http://www.britishaudio.co.uk/SPR-SPUR3.html

    Interesting they use fuses instead of circuit breakers. Do fuses really sounds better?

    Oh, and what sockets to use? US Hubbell, Euro Schuko or 15amp Round Pin UK?
     
    HenryT, Jul 14, 2003
    #11
  12. penance

    themadhippy seen it done it smokin it

    Joined:
    Jun 19, 2003
    Messages:
    1,118
    Likes Received:
    1
    Location:
    by the cross
    £30.27 for the consumer unit,£15.08 for the input fuse,and £4.53 for each output fuse, comes to er around £72 for a 6 way unit,prices from http://www.neweyandeyre.co.uk/.and do a search for Memera 2000

    As for what socket why not BS4343,16A plug and sockets?
    [​IMG]
     
    Last edited by a moderator: Jul 15, 2003
    themadhippy, Jul 15, 2003
    #12
  13. penance

    wadia-miester Mighty Rearranger

    Joined:
    Jun 19, 2003
    Messages:
    6,026
    Likes Received:
    0
    Location:
    Beyond the 4th Dimension
    I have to say I thought those B/D prices were a bit steep :eek:
    I love to see a wall recepticle or plug being annealed :D might have a forum competition to see who can use it after :cool:
    I reckon you been browsing the WAD forum too much!!!!
    this stuff might be worth a go ;) really expensive too
    This stuff is pretty good and not too dear.

    http://www.virtualdynamics.ca/products/HWS/ABX

    How you terminate is up to you, but bear in mind if you swopping a lot of stuff, then go for a common & interchangable end.
     
    wadia-miester, Jul 15, 2003
    #13
  14. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    Hippy, i probably will use a henly box, as you say, its the easiest way.
    Only reason for a seperate earth was thinking it may produce better results:confused:

    I may use 15A round pin, not sure yet, does it really give an audible difference?
     
    penance, Jul 15, 2003
    #14
  15. penance

    tones compulsive cantater

    Joined:
    Jun 19, 2003
    Messages:
    3,021
    Likes Received:
    0
    Location:
    Switzerland
    It's mains again
    It really goes 'gin the grain
    I know I'm losing again
    I change my cables in vain

    C'mon, you little cable
    Do what I know you're able
    And give an image stable
    'Cos I can't stand the pain
    Babababaaaaaaaaa.....

    (sorry...)
     
    tones, Jul 15, 2003
    #15
  16. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.
    :D

    LMAO

    :D
     
    penance, Jul 15, 2003
    #16
  17. penance

    Chea Johndle Bizarre Serpent Foomaster

    Joined:
    Jun 19, 2003
    Messages:
    217
    Likes Received:
    0
    Location:
    Foo Central
    No, No, No....

    Be VERY sorry:D


    Regards
     
    Chea Johndle, Jul 15, 2003
    #17
  18. penance

    tones compulsive cantater

    Joined:
    Jun 19, 2003
    Messages:
    3,021
    Likes Received:
    0
    Location:
    Switzerland
    Believe me, I am, truly, I am....
     
    tones, Jul 15, 2003
    #18
  19. penance

    penance Arrogant Cock

    Joined:
    Jun 30, 2003
    Messages:
    6,004
    Likes Received:
    2
    Location:
    Bristol - armpit of the west.

    for your penance you can come and drill the holes thru my wall;)
     
    penance, Jul 15, 2003
    #19
  20. penance

    tones compulsive cantater

    Joined:
    Jun 19, 2003
    Messages:
    3,021
    Likes Received:
    0
    Location:
    Switzerland
    No sweat! Mighty Metabo, my electropneumatic hammer, will have your wall for breakfast. (One needs such things in Switzerland, where everything below ground level is very solid concrete)
     
    tones, Jul 15, 2003