Father drilled a mains cable - is this legal under current wiring regulations

amazingtrade

Mad Madchestoh fan
Joined
Jun 19, 2003
Messages
5,139
Reaction score
0
Location
Manchester
My dad was drilling through a door frame (top bit) and drilled through a cable. All the electricity went off bypassing the consumer unit and blowing the electricity boards fuse that comes into the house.

I isolated the circuit and they replaced the fuse no problems but I have a couple of worries

1) The correct fuse was installed in the consumer unit - why didn't this blow?

2) Is it legal to have wires behind a door frame in the first place? The house was rewired in 1980.

3) I have also noticed a lot of back boxes (metal ones) do not have the earth fly lead attached, so when I replace sockets I always add this (using the correct insulation sleeve) and I also wondered if this was legal back in 1980.

Thaks.
 
check the building regs, there are specs on all this, i thought it was minimum 6 inches from any edge or corner.
 
1) The correct fuse was installed in the consumer unit - why didn't this blow
disconection times and fault currents dear boy,each type of fuse/mcb will operate in a certain time at a certain fault current,each type of protective device has a diffrent fault/time characteristic
2) Is it legal to have wires behind a door frame in the first place? The house was rewired in 1980
yep,as the wiring regs aint a statutory code,however it aint good practise
3) I have also noticed a lot of back boxes (metal ones) do not have the earth fly lead attached, so when I replace sockets I always add this (using the correct insulation sleeve) and I also wondered if this was legal back in 1980
as above,but it was at one time common not to bother with the box earth, the screws holding the face plate on would do the job for you was the attitude of many sparkys,especially on lighting circuits were its not uncommon on older installations not to bother with an earth either
 